ML
    • Recent
    • Categories
    • Tags
    • Popular
    • Users
    • Groups
    • Register
    • Login

    Odd Shaped Power Bricks and UPS

    IT Discussion
    9
    29
    2.5k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • BRRABillB
      BRRABill
      last edited by

      So, we got dinged by the fire department the other day for having a power strip into a UPS.

      I've been doing a little research, and it appears that the UPS manufacturers themselves recommend against this. (OF course, to sell more UPSes!)

      Anyway. I was wondering what setups you all have for oddly shaped power bricks that would work great in a power strip, but take up too much room in a UPS.

      J 1 Reply Last reply Reply Quote 1
      • DashrenderD
        Dashrender
        last edited by

        This is funny.

        The few datacenters I've been in that had UPSs in the rack, had Power Strips running up the sides of the rack where the servers plugged into.

        So are those doing it wrong also?

        J 1 Reply Last reply Reply Quote 0
        • J
          Jason Banned @BRRABill
          last edited by

          @BRRABill said in Odd Shaped Power Bricks and UPS:

          I've been doing a little research, and it appears that the UPS manufacturers themselves recommend against this. (OF course, to sell more UPSes!)

          Daisy chaining any UPS, Power Tap, Surge Protector etc. Is always not allowed unless what's plugg into it has over current protection and even then it's frowned upon.

          1 Reply Last reply Reply Quote 2
          • J
            Jason Banned @Dashrender
            last edited by

            @Dashrender said in Odd Shaped Power Bricks and UPS:

            This is funny.

            The few datacenters I've been in that had UPSs in the rack, had Power Strips running up the sides of the rack where the servers plugged into.

            So are those doing it wrong also?

            The powerstrips in data centers have overcurrent protection.

            1 Reply Last reply Reply Quote 1
            • BRRABillB
              BRRABill
              last edited by

              The problem(s) I have is ...

              1. the current server room is poorly wired with access to electrical boxes
              2. some of the equipment I have in there has strange "the wrong way" power blocks

              I could re-use an older UPS, I guess. I'm just wondering, as I said, what others are doing.

              dafyreD 1 Reply Last reply Reply Quote 0
              • J
                Jason Banned
                last edited by

                What in the server room has wall warts? Most things use IEC cables direct or a Brick with an IEC to it.

                BRRABillB 1 Reply Last reply Reply Quote 0
                • dafyreD
                  dafyre @BRRABill
                  last edited by

                  @BRRABill said in Odd Shaped Power Bricks and UPS:

                  The problem(s) I have is ...

                  1. the current server room is poorly wired with access to electrical boxes
                  2. some of the equipment I have in there has strange "the wrong way" power blocks

                  I could re-use an older UPS, I guess. I'm just wondering, as I said, what others are doing.

                  That's odd. We never got dinged for it at my last job. (Granted, we didn't use the $7 Dollar General special either).

                  And at my current job, we use power bars made specifically for use in server racks. (these, I assume have the overcurrent protection, etc, etc).

                  BRRABillB 1 Reply Last reply Reply Quote 0
                  • BRRABillB
                    BRRABill @Jason
                    last edited by

                    @Jason said in Odd Shaped Power Bricks and UPS:

                    What in the server room has wall warts? Most things use IEC cables direct or a Brick with an IEC to it.

                    I have a couple of small switches in there with strange wall warts.

                    J 1 Reply Last reply Reply Quote 0
                    • J
                      Jason Banned @BRRABill
                      last edited by

                      @BRRABill said in Odd Shaped Power Bricks and UPS:

                      @Jason said in Odd Shaped Power Bricks and UPS:

                      What in the server room has wall warts? Most things use IEC cables direct or a Brick with an IEC to it.

                      I have a couple of small switches in there with strange wall warts.

                      I would replace the switches then..

                      BRRABillB 2 Replies Last reply Reply Quote 0
                      • BRRABillB
                        BRRABill @dafyre
                        last edited by

                        @dafyre said in Odd Shaped Power Bricks and UPS:

                        @BRRABill said in Odd Shaped Power Bricks and UPS:

                        The problem(s) I have is ...

                        1. the current server room is poorly wired with access to electrical boxes
                        2. some of the equipment I have in there has strange "the wrong way" power blocks

                        I could re-use an older UPS, I guess. I'm just wondering, as I said, what others are doing.

                        That's odd. We never got dinged for it at my last job. (Granted, we didn't use the $7 Dollar General special either).

                        And at my current job, we use power bars made specifically for use in server racks. (these, I assume have the overcurrent protection, etc, etc).

                        They haven't checked in a while, and I think maybe they were just looking to ding people.

                        I also got dinged for not having ceiling tiles in our wiring room.

                        J 1 Reply Last reply Reply Quote 0
                        • BRRABillB
                          BRRABill @Jason
                          last edited by

                          @Jason said in Odd Shaped Power Bricks and UPS:

                          @BRRABill said in Odd Shaped Power Bricks and UPS:

                          @Jason said in Odd Shaped Power Bricks and UPS:

                          What in the server room has wall warts? Most things use IEC cables direct or a Brick with an IEC to it.

                          I have a couple of small switches in there with strange wall warts.

                          I would replace the switches then..

                          A definite possibility!

                          1 Reply Last reply Reply Quote 0
                          • DustinB3403D
                            DustinB3403
                            last edited by

                            Or just find a better power adapter for the switch, one that will provide the correct power output, and fit in your UPS.

                            1 Reply Last reply Reply Quote 0
                            • J
                              Jason Banned @BRRABill
                              last edited by Jason

                              @BRRABill said in Odd Shaped Power Bricks and UPS:

                              I also got dinged for not having ceiling tiles in our wiring room.

                              That is normal if you have a drop ceiling. It's for a fire(smoke)/air barrier.

                              1 Reply Last reply Reply Quote 1
                              • gjacobseG
                                gjacobse
                                last edited by

                                I wonder if something of this sort would be allowed.... It's not a power strip. just power cords that are about a foot long to allow connection to the adapters.

                                http://i.stack.imgur.com/8zW2l.jpg

                                J 1 Reply Last reply Reply Quote 1
                                • DashrenderD
                                  Dashrender
                                  last edited by

                                  I bet they would be. I'm sure the primary concern, as Jason rightly pointed out, was the overdrawn issue.

                                  1 Reply Last reply Reply Quote 0
                                  • J
                                    Jason Banned @gjacobse
                                    last edited by Jason

                                    @gjacobse said in Odd Shaped Power Bricks and UPS:

                                    I wonder if something of this sort would be allowed.... It's not a power strip. just power cords that are about a foot long to allow connection to the adapters.

                                    http://i.stack.imgur.com/8zW2l.jpg

                                    No over current protection. Also this type device in a commerical setting falls under extension cord restrictions, which OSHA only allows temporary use of. Now if they are UL Listed for being plugged into a power strip in that manner it would be allowed.. (hence how C13 extensions are allowed) but otherwise they would have to be plugged directly into a wall outlet.

                                    1 Reply Last reply Reply Quote 0
                                    • J
                                      Jason Banned
                                      last edited by

                                      EX: https://www.amazon.com/Solid-Cordz-Female-Extension-Cords/dp/B00CG70K78/ref=cm_cr_dp_asin_lnk

                                      These are UL listed but likely not for that use.

                                      1 Reply Last reply Reply Quote 0
                                      • BRRABillB
                                        BRRABill
                                        last edited by

                                        Yeah these particular switches (workgroup Cisco SG-200-8) can't take that sort of plug.

                                        1 Reply Last reply Reply Quote 0
                                        • DashrenderD
                                          Dashrender
                                          last edited by

                                          I'm assuming @gjacobse is talking about the black cord only.
                                          https://i.imgur.com/oCkdbBE.png

                                          I don't know OSHA law/rules, but there should be no need to check for over current in the black part, it's a 1 to 1 connection. Assuming you plug the 1 to 1 and it's plugged directly into a UPS port, not a power strip like this picture.

                                          gjacobseG J 2 Replies Last reply Reply Quote 0
                                          • gjacobseG
                                            gjacobse @Dashrender
                                            last edited by

                                            @Dashrender said in Odd Shaped Power Bricks and UPS:

                                            I'm assuming @gjacobse is talking about the black cord only.
                                            https://i.imgur.com/oCkdbBE.png

                                            I don't know OSHA law/rules, but there should be no need to check for over current in the black part, it's a 1 to 1 connection. Assuming you plug the 1 to 1 and it's plugged directly into a UPS port, not a power strip like this picture.

                                            Correct. YOu would not use the power strip as you are using an UPS. Just use the cords to connect the adapter to the UPS as normal.

                                            1 Reply Last reply Reply Quote 0
                                            • 1
                                            • 2
                                            • 1 / 2
                                            • First post
                                              Last post